What is the maximum transfer capability of the following


Problem 1 (Computing Critical Clearing Time (CCT) using EAC):

A three-phase 50 Hz synchronous generator is supplying power through pure reactive parallel transmission lines to an infinite bus. The machine is delivering 1.0 per unit power ( ) before a three phase short circuit fault occurs in the system.

The mechanical power is Pm=1.1pu, Eq'=1.1pu and the per unit inertia constant H=10 MJ/MVA. Figure 1 shows the power angle characteristics before, during and after the fault with all values in pu:

495_function.png

Compute:

a) The steady-state power angle δ0.

b) The maximum power angle δmax.

c) The critical clearing angle δcr.

d) Compute the critical clearing time tcr(in sec).

e) If the clearance time can be reduced to 120msec, what is the maximum power that this machine can deliver while remaining stable?

f) If the generator is required to supply 1.1 pu load with the critical fault clearance time as calculated in section (d), propose possible options to ensure the generator remains stabile.

6_after the fault.png

Figure 1. The power angle characteristics before, during and after the fault for Question 1 with all values in pu.

Problem 2:

Find the equation for the Synchronizing Torque Coefficient of the following system around the operating point δ = δ0

1371_Torque Coefficient.png

Problem 3:

Derive the state equation of the following system in form:

Δx· = A Δx+B Δu   Δy = C Vx + DΔu

240_system.png

 

933_digital computer.png

Problem 4:

What is the maximum transfer capability of the following system to supply a constant PQ load at 0.8 lag power factor? How much can this transfer capability be increased by installing capacitor banks?

The System voltage at normal operational condition is within a range of 0.9pu-1.1pu.

2271_System voltage.png

Solution Preview :

Prepared by a verified Expert
Electrical Engineering: What is the maximum transfer capability of the following
Reference No:- TGS01147398

Now Priced at $60 (50% Discount)

Recommended (96%)

Rated (4.8/5)

A

Anonymous user

5/28/2016 8:27:03 AM

The problem illustrated here mainly based on calculating the critical clearing time (CCT) by using the EAC. Question: A 3-phase 50 Hz synchronous generator is supplying power via pure reactive parallel transmission lines to the infinite bus. The machine is delivering 1.0 per unit power before a 3-phase short circuit fault takes place in the system. The mechanical power is Pm=1.1pu, Eq'=1.1pu and the per unit inertia constant H=10 MJ/MVA. Figure illustrates the power angle characteristics before, throughout and after the fault by means of all values in pu. Calculate: 1) Steady-state power angle d0. 2) Maximum power angle dmax. 3) Critical clearing angle dcr. 4) Calculate the critical clearing time tcr(in sec). 5) If the clearance time can be decreased to 120msec, determine the maximum power that this machine can bring while remaining stable?