Two parallel connected 10 kV to 120 V 60 Hz single phase transformers supply a varying load.
Transformer 1, Rating 60 kVA, parameters referred to primary:
Rc=250 k Ohm
Req=25 Ohm
Xm=45 k Ohm
Xeq=150 Ohm
Transformer 2, Rating 30 kVA, parameters referred to primary:
Rc=400 k Ohm
Req=30 Ohm
Xm=90 k Ohm
Xeq=300 Ohm
Assuming 0.85 PF, what is the maximum load current that can be supplied by this parallel combination of transformers wihout overloading either of them?