The primary and secondary winding of a three-phase transformer rated at 400/230 kV are both wye-connected. Calculate the primary and secondary turns of each phase, knowing that the insulation between two consecutive turns can sustain 50 V. Determine also the rated primary and secondary line currents, if the rated power is 250 MVA.