The no-load voltage of a y-connected synchronous generator


The no-load voltage of a Y-connected synchronous generator is 3646V. When the generator delivers the rated load of 432kW at 0.8pf lagging, the terminal voltage is 3117.69V. If the armature winding resistance is negligible, determine the synchronous reactance of the generator. When the load is changed to 80 + j60 per phase, determine the terminal line to line voltage.