The new loaf will add 600kw to the real power load of the


A factory has an electrical load of 1,800kW at a lagging power factor of 0.6. An additional variable power factor load is to be added to the factory. The new loaf will add 600kW to the real power load of the factory. The power factor of the added load is to be adjusted so that the overall power factor of the factory is 0.96 lagging.
a) Specify the reactive power associated with the added load?

b) Does the added load absorb or deliver magnetizing vars?

c) What is the power factor of the additional load?

d) Assume that the rms voltage at the input of the factory is 480 V. What is the rms magnitude of the current into the factory before the variable power factor load is added?

e) What is the rms magnitude of the current into the factory after the variable power factor load has been added?

Request for Solution File

Ask an Expert for Answer!!
Electrical Engineering: The new loaf will add 600kw to the real power load of the
Reference No:- TGS0616626

Expected delivery within 24 Hours