q. two shunt wound generators running in


Q. Two shunt wound generators running in parallel supply a total load current of 4000 A. Each generator has an armature resistance of 0.02? and a field of 40?. The fiels are excited so that the emf induced in one generator is 480 V and in another 490 V, find the bus - bar voltage and kilowatt output of each machine.

 

Sol.            V = bus bar voltage

 

                  I1 = current output of generator 1

 

                  I2 = current output of generator 2

 

             I1 + I2 =  4000

               Ish = V/Rsh

 

       Bus - bar voltage

 

       In each machine

 

       Bus bar voltage + voltage

 

       Drop in armature = EMF generated

 

       for  generated 1, E1 = V + Ia1 Ra

 

                 480 = V + (I1 + V/40) × 0.02

 

               (Ia1 = I1 + Ish)

 

      for  generated 2 490 =  V + (I2 + V/40) × 0.02

 

      Subtrating both with each other we get,

 

            0.0212 - 0.0211 = 10

 

  or      I2 - I1 = 500

 

  or      (4000 - I1) - I1 = 500

 

             I1 = 1750A and I2 = 4000 - 1750 = 2250A

 

Now          480 = V + (I1 + V/40) × 0.02    or      490 =  V + (I2 + V/40) × 0.02

 

                On solving V = 444.8 volts

 

           Kilowatt output

 

               kW output of gen. 1, VI1/1000 = 444.8 × 1750/1000 = 778.4kW

 

               kW output of gen. 2, VI1/1000 = 444.8 × 2250/1000 = 1001kW 

Request for Solution File

Ask an Expert for Answer!!
Electrical Engineering: q. two shunt wound generators running in
Reference No:- TGS0157239

Expected delivery within 24 Hours