Q. Local operator panel for steam generator?
A local operator's panel is required for operator use during Steam Generator light off. This panel shall contain the following equipment as a minimum:
• Status sequence lights
• Flame safeguard management system and flame strength meter
• Burner Switch
• Reset button
During Steam Generator light off, the operator shall be at the local control panel and in communication with the control room operator. Upon initiation of start-up, the operator will wait for the signal that the permissive start valve can be opened.