If these transformers are connected in parallel to supply a


Transformer A is rated at 300 KVA with an impedance of (0.09+j0.18)ohms Transformer

Transformer A is rated at 300 KVA with an impedance of (0.09+j0.18)ohms

Transformer B is rated at 200KVA with an impedance of (0.09+j0.23)ohms

If these transformers are connected in parallel to supply a common load,determine the percentage overload on B when A supplies its full load at p.f.0.45 lag.