Find the generator terminal voltage in kv and the real


Consider a three-phase generator rated 300 MVA, 23 kV, supplying a system load of 240 MVA and 0.9 power factor lagging at 230 kV through a 330 MVA, 23 ?/ 230 Y-kV step-up transformer with a leakage reactance of 0.11 per unit.

(a) Neglecting the exciting current and choosing base values at the load of 100 MVA and 230 kV, find the phasor currents IA, IB, and IC supplied to the load in per unit.

(b) By choosing the load terminal voltage VA as reference, specify the proper base for the generator circuit and determine the generator voltage V as well as the phasor currents Ia, Ib, and Ic, from the generator. (Note: Take into account the phase shift of the transformer.)

(c) Find the generator terminal voltage in kV and the real power supplied by the generator in MW.

(d) By omitting the transformer phase shift altogether, check to see whether you get the same magnitude of generator terminal voltage and real power delivered by the generator.

Request for Solution File

Ask an Expert for Answer!!
Other Engineering: Find the generator terminal voltage in kv and the real
Reference No:- TGS01525468

Expected delivery within 24 Hours