Saturated R-134a vapor enters a steady-flow, adiabatic compressor at 180 kPa and is compressed to 700 kPa, 50°C. The power supplied to the compressor is 2.5 kW. Determine the volume flow rate of the refrigerant at both the inlet and exit to the compressor, in m3/min.