Determine a suitable value of neutral resistance if the


An 11 kV motor is fed by cables from a transformer via switchgear, having a phase impedance of 0.3 + j0.3 ohm. The earth return path to the transformer neutral has a resistance of 0.42 ohm. Determine a suitable value of neutral resistance if the voltage rise at the motor in the event of an earth fault at the motor is not to exceed 430 V. Neglect transformer winding resistance.