Problem 1: An overhead line is supported between two towers. The base of Tower A is 185m above sea level and the tower is 25m high. Tower B base is at 200m above sea level and the tower is 35m high. The distance between the towers is 350m. The conductor weight is 32N/m and the tension at the tower is 35kN. At what height above sea level is the lowest point of the conductor, assuming that xW << To so that the approximation y = x2W/2To may be used.
Problem 2: A 400V symmetrical three phase source with grounded neutral supplies a load comprising three impedances in star formation. The impendence have the following values:
Za = 20Ω
Zb = (12 + j5)Ω
Zc = (3 - j4)Ω
Calculate the total active and reactive power supplied to the load both with and without the load star point grounded.
Problem 3: While on a walk in the countryside, you come across a fallen HV conductor which, due to a protection failure, has not tripped. If the HV system is solidly grounded, explain how the fault current presents a danger to you. Would this danger still be present if the system was arc-suppressed?